APC UPS - driver messed up (solved)
« on: April 09, 2007, 09:42:06 PM »
I'd like to know if anybody has had a similar problem and if so, they think that excess heat might be my problem.

This morning I received the following email message from my test server

Quote
Communications with UPS UPS@localhost lost


followed by this email every 5 minutes

Quote
UPS UPS@localhost is unavailable


When I went to the room where the server, and a bunch of other equipment, is located I found that it was 32 degrees C. The APC website says up to 40C. I rebooted everything and opened the door to the room.

My next emails were one right after the other;
Quote
Communications with UPS UPS@localhost established


and then

Quote
Communications with UPS UPS@localhost lost


However, it did not repeat itself.

I log in as root and run the following code and get the following answer, so everything looks ok.
Quote

[root@mailbox1 ~]# upsc UPS@192.168.1.***
battery.charge: 100
battery.chemistry: PbAc
battery.runtime: 2827
battery.voltage: 1.2
driver.name: hidups
driver.parameter.port: /var/lib/ups/hiddev0
driver.version: 2.0.5
ups.delay.shutdown: -1
ups.load: 18
ups.mfr: American Power Conversion
ups.model: Back-UPS RS 1000 FW:7.g8 .D USB FW:g8
ups.serial: JB0406007106
ups.status: OL
[root@mailbox1 ~]#

Offline pfloor

  • ****
  • 889
  • +1/-0
Re: APC UPS - too hot?
« Reply #1 on: April 10, 2007, 07:09:34 PM »
Quote from: "imcintyre"
I log in as root and run the following code and get the following answer, so everything looks ok.
Quote

[root@mailbox1 ~]# upsc UPS@192.168.1.***
battery.charge: 100
battery.chemistry: PbAc
battery.runtime: 2827
battery.voltage: 1.2
driver.name: hidups
driver.parameter.port: /var/lib/ups/hiddev0
driver.version: 2.0.5
ups.delay.shutdown: -1
ups.load: 18
ups.mfr: American Power Conversion
ups.model: Back-UPS RS 1000 FW:7.g8 .D USB FW:g8
ups.serial: JB0406007106
ups.status: OL
[root@mailbox1 ~]#

That does not look OK.

-driver.name: hidups <This is an old depreciated driver, you shouldn't use it. Use newhidups instead.
-There should be more information (My RS 1500 has 30 lines).
-battery.voltage: 1.2 <This is not correct, AFAIK all RS model use a 24 volt battery setup.

Did you change the default configuration?  What does this show (remove your passwords please)?
Code: [Select]
config show nut
In life, you must either "Push, Pull or Get out of the way!"

Offline imcintyre

  • *
  • 609
  • +0/-0
APC UPS - driver messed up (solved)
« Reply #2 on: April 10, 2007, 10:10:29 PM »
Thanks for your help

As requested:
Quote
[root@myserver ~]# config show nut
nut=service
    Model=hidups
    status=enabled
[root@myserver ~]#


I also ran the uspc command to see if anything changed:
Quote

[root@myserver ~]# upsc UPS@192.168.1.***
battery.charge: 100
battery.chemistry: PbAc
battery.runtime: 2745
battery.voltage: 1.2
driver.name: hidups
driver.parameter.port: /var/lib/ups/hiddev0
driver.version: 2.0.5
ups.delay.shutdown: -1
ups.load: 19
ups.mfr: American Power Conversion
ups.model: Back-UPS RS 1000 FW:7.g8 .D USB FW:g8
ups.serial: JB0406007106
ups.status: OL
[root@mailbox1 ~]#


As an aside, what are those passwords doing there? and what are they the passwords for?

Offline imcintyre

  • *
  • 609
  • +0/-0
APC UPS - driver messed up (solved)
« Reply #3 on: April 10, 2007, 10:27:53 PM »
As recommended, I changed the driver with the following result.

Quote

[root@myserver ~]# config setprop nut status disable
[root@myserver ~]# config setprop nut Model newhidups
[root@myserver ~]# config setprop nut status enabled
[root@myserver ~]# config show nut
nut=service
    Model=newhidups
    status=enabled
[root@myserver ~]# expand-template /etc/sysconfig/ups
[root@myserver ~]# expand-template /etc/ups/ups.conf
[root@myserver ~]# expand-template /etc/ups/upssched.conf
[root@myserver ~]# expand-template /etc/ups/upsmon.conf
[root@myserver ~]# expand-template /etc/ups/upsd.users
[root@myserver ~]# expand-template /etc/ups/upsd.conf
[root@myserver ~]#  /etc/rc7.d/S15nut restart
Stopping UPS monitor:                                      [  OK  ]
Stopping upsd:                                             [  OK  ]
Shutting down upsdrvctl: Network UPS Tools - UPS driver controller 2.0.5
Can't open /var/run/nut/newhidups-UPS.pid: No such file or directory

Starting upsdrvctl:                                        [  OK  ]
Starting upsd:                                             [  OK  ]
Starting UPS monitor (master):                             [  OK  ]
[root@myserver ~]# config show nut
nut=service
    Model=newhidups
    status=enabled
[root@myserver ~]# upsc UPS@192.168.1.***
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.date: 2001/09/25
battery.mfr.date: 2004/02/03
battery.runtime: 2745
battery.runtime.low: 120
battery.type: PbAc
battery.voltage: 26.9
battery.voltage.nominal: 24.0
driver.name: newhidups
driver.parameter.port: /var/lib/ups/hiddev0
driver.version: 2.0.5
driver.version.data: APC/CyberPower HID 0.9
driver.version.internal: 0.30
input.transfer.high: 138
input.transfer.low: 97
input.voltage: 120.0
input.voltage.nominal: 120
ups.beeper.status: disabled
ups.delay.shutdown: -1
ups.firmware: 7.g8 .D
ups.firmware.aux: g8
ups.load: 19
ups.mfr: American Power Conversion
ups.mfr.date: 2004/02/03
ups.model: Back-UPS RS 1000
ups.serial: JB0406007106
ups.status: OL
ups.test.result: No test initiated
[root@myserver ~]#


Given your comments about the voltage, this looks better, although I am uncertain about the line:
Quote
Can't open /var/run/nut/newhidups-UPS.pid: No such file or directory


I can look around for this line but is it something you recognize as legit?

Quote
Edit: Zaro boogs found


Thx again

Offline pfloor

  • ****
  • 889
  • +1/-0
APC UPS - driver messed up (solved)
« Reply #4 on: April 10, 2007, 10:47:21 PM »
Quote
As an aside, what are those passwords doing there? and what are they the passwords for?

Those are there so you can configure master/slave servers connected to the same UPS if you want.

Quote
Can't open /var/run/nut/newhidups-UPS.pid: No such file or directory

This is caused because the driver stops and starts too fast.  There is/was a bug on the issue but I beleive it has been fixed but not yet released.  You can avoid the error by issuing a "stop" wait 5 seconds and then "start" instead of restart.
In life, you must either "Push, Pull or Get out of the way!"

Offline imcintyre

  • *
  • 609
  • +0/-0
APC UPS - driver messed up (solved)
« Reply #5 on: April 10, 2007, 11:46:30 PM »
Great, I really appreciate your help. It seems to be working perfectly. I unplugged the device, waited a minute then plugged it back in and received emails telling me that it was on battery and then back on line.

I did read a post that stated a "signal event post upgrade and a signal post event reboot" was required, but that would seem to not be the case.
Is this the case or not?

Thx in advance.

Offline pfloor

  • ****
  • 889
  • +1/-0
APC UPS - driver messed up (solved)
« Reply #6 on: April 11, 2007, 12:03:11 AM »
Quote from: "imcintyre"
Great, I really appreciate your help. It seems to be working perfectly. I unplugged the device, waited a minute then plugged it back in and received emails telling me that it was on battery and then back on line.

I did read a post that stated a "signal event post upgrade and a signal post event reboot" was required, but that would seem to not be the case.
Is this the case or not?

Thx in advance.
post-upgrade/reboot required for what?

It is required for certian things but not *usually* for configuration changes (there are a few exceptions).  It is usually required for software installs/updates, especially if the package starts with "smeserver-" or "e-smith-".

When in doubt, you can safely post-upgrade/reboot any time.